We were trying out a used portable generator we recently purchased, on a hog facility. Its a 1997 CAT with 8900 hrs. It still looks great despite all those hours. the generator size on the nameplate reads 100 KVA, 50 KW at 0.5 PF, 278 Amps at 208Y/120V . Really curious why KW is rated at 0.5 PF. All generators I've seen are rated at 0.8 PF. So its really an 80 KW.
Anyways, facility voltage is 208Y/120v 3 ph. During test run, load was reasonably balanced and average current on phases was about 115 Amps. then went inside and tried out the 20 HP pressure pump. The voltage dipped so much the lights actually went out for a second or too, then the motor ran uneven for about 3 seconds before running normally. Per NEC, 20 HP motor at 208 FLA is 59 amps, and LRA is 321. Is the inrush too much for a 80 KW generator, or is something wrong with it? we had problems with it at first with fluctuating voltage under minimum load but we changed the fuel filters and that really improved things.
Anyways, facility voltage is 208Y/120v 3 ph. During test run, load was reasonably balanced and average current on phases was about 115 Amps. then went inside and tried out the 20 HP pressure pump. The voltage dipped so much the lights actually went out for a second or too, then the motor ran uneven for about 3 seconds before running normally. Per NEC, 20 HP motor at 208 FLA is 59 amps, and LRA is 321. Is the inrush too much for a 80 KW generator, or is something wrong with it? we had problems with it at first with fluctuating voltage under minimum load but we changed the fuel filters and that really improved things.