bobrosen
New User
- United States
3 phase 208 volt swimming pool pumps
do they require gfi protection?
I have never used one but Square does have 3 pole QO series GFCI's in the catalog for 15, 20, 30, 40 and 50 amp trip settings.Where are you going to get a 3 phase breaker that is gfci? I don't believe one is available however since there is this product http://207.56.194.41/LG100_GFCI.pdf perhaps it may change in the code one day but I doubt it. The 2014 does not require gfci either.
So what the code is telling us is that only single phase pool pumps operating at a voltage between 120 and 240 volts can fail in a manner that can cause harm to people using the pool.
Was there any evidence that pool pumps were a safety issue or was it simply someone's notion that it would be good thing to do?So what the code is telling us is that only single phase pool pumps operating at a voltage between 120 and 240 volts can fail in a manner that can cause harm to people using the pool.
That never stopped them in the past from introducing AFCI requirements involving devices that were not all that readily available at the time, and they even published an effective date in the code to give time to make products available:roll:Or that at the time that section was written, GFCI devices were only available in that limited range?
Tapatalk!