Hi all!  I'm a new member to this forum but boy am I glad I found it.  If there are any electrical inspectors on here I'd really love your thoughts on this but any comments are appreciated.
Here's my dilemma. We recently were presented with an option to retrofit all ~4000 of the HID lights in our greenhouses to LED panels that were supposedly designed for greenhouse installations. The problem is I'm getting two decidedly different opinions from several different LED Grow Light manufacturers as to whether or not the lights themselves are rated for a damp location environment. So here are the different mfg's we have to choose from and the methods of construction they employ:
Illumitex states an IP66 rating and is listing this on their spec sheets.
http://www.illumitex.com/wp-content/uploads/2012/08/Spec_NeoSolNS081412.pdf
When I asked Apache Tech about this I've copied and pasted their response below this link
http://www.apachetechinc.com/white-red/25-at600.html
Now after reading this response I am more confused then ever. If I were involved in manufacturing an LED panel for greenhouses it would seem that having it rated for that environment would be high on my list of objectives. My concern is that Section 314-16 is not being met. The fact that the ApacheTech panels, as well as others such as Lumigrow, utilize active cooling fan enclosures as opposed to the passively cooled bars like Illumitex and are not expressly listed for damp locations would give an inspector every right to not pass the job since the listing agency does not show this product as Damp Location rated.
http://www.lumigrow.com/documents/Pro-Fixture-DataSheet-EN.pdf
and finally Phillips who rates all of their LED lights as IP66 rated for these environments.
http://www.google.com/url?sa=t&rct=...rV7MYpJrB1u0J2A&bvm=bv.61535280,d.aWc&cad=rja
So as our commercial agriculture industry decides to take advantage of lower watts/sq ft technologies it's important that we do so with the best lighting and controls necessary to maintain optimum crop production values. The LED panel mfg's are offering expensive retrofit solutions that propose longer life spans and lower operating watts but are also giving us conflicting messages on everything about how much energy they produce within given PAR (spectral) regions to whether or not the panels are even rated for the environment we'll be using them in. I don't want to invest this kind of money and be wrong. At least if I know how inspecting authorities view this it will help.
Of note our current lights are 1000watt HPS lights by PAR Source and they say right on their spec sheets they are sealed ballasts for greenhouse environments.
http://parsource.com/sites/default/...nic)_Sales_Sheets_GLE1277 Updated 1.17.14.pdf
So after considering all of the above I am left to believe that this is at best may be a grey area that needs defining and at worst is a misrepresentation by some of the panel manufacturers to capitalize on these retrofit programs without regard to how inspecting authorities might rule on their being properly listed for the environment. I do know that when I go to do a UL search on other equipment that is installed inside the greenhouses it will state it is listed for damp locations. Are the LED panel manufacturers being given a pass somehow?
Good morning,
We have not subjected our lights to this testing protocol. This is a protocol primarily utilized by the UK and the EC, and it has gained acceptance here in the US and we can see it's usefulness. However, this is not a UL certification process. UL has their own and has deemed our lights appropriate for wet locations. We may consider submitting the lights to this testing procedure in the future, but have no immediate plans to do so. Our lights were designed to work effectively and safely in the rigorous environments of controlled environmental chambers (>99% RH), over the top of public aquariums (100% RH, salt intrusion and high amounts of splashing) and in greenhouses (High temperatures, high humidity and splashing) and have been UL qualified and accepted for all environments. All chips are sealed in a water tight enclosure, fans are designed for wet conditions, power supplies are epoxy sealed and connectors are all waterproof. If jets of water penetrate the housing (which is possible), no damage will occur to the product (this is what IP ratings are concerned with). UL certification is concerned with the "user" and how safe they are working around the product. I'm also certain GFI's are a must in this construction.
Bottomline, is that we do not have an official IP certification number and you are the first client that has ever actually requested one. Our lights have passed the scrutiny and safety measures required by prestigious universities, government research agencies, some of the large commercial corporations and some of the largest public aquariums in the world. No HPS or MH lighting fixture would meet this requirement either, with the exception of some lighting systems with additional and very expensive additional housings around the light and ballast.
The Illumitex bars are really good lights and it sounds like this might be the proper answer for your client. Light bar technology will provide this type of protection. Illumitex make a very good product, but do not come close to our lights in intensity and footprint. Apache Tech LED is the only agricultural LED that has a greater light intensity and equal footprint as a 1000W HPS.
btw, sulfur burners are no problem.
Sorry we could not get you the certification you were looking for and good luck with your project!