Does a transformer with an ungrounded delta secondary need to be bonded to CWP or building steel?
R rcontreraspe Member Location Anaheim, CA Feb 20, 2014 #1 Does a transformer with an ungrounded delta secondary need to be bonded to CWP or building steel?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Feb 20, 2014 #2 The only thing different between a grounded and ungrounded secondary is that the ungrounded one will not have a system bonding jumper. All of the other grounding and bonding rules are the same.
The only thing different between a grounded and ungrounded secondary is that the ungrounded one will not have a system bonding jumper. All of the other grounding and bonding rules are the same.