PV wire is sunlight resistant. How many hours of direct sunlight can sunlight resistant wire take before the insulation breaks down? I can not find a definition for Sunlight Resistant.
For an optional marking of sunlight resistant, the conductors covered by UL 44 and UL 83 are required to meet the requirements of 720-hour carbon-arc or xenon- arc exposure tests.
I have looked at UL and can't find anything.I also found this but I don't have the UL standards--Not sure that will even give you an answer
I have looked at UL and can't find anything.
Seems I remember that RHW-use 2 was rated as sunlight resistant to 300 hours.
PV wire is supposed to be better, but how much better?
I have looked at UL and can't find anything.
Seems I remember that RHW-use 2 was rated as sunlight resistant to 300 hours.
PV wire is supposed to be better, but how much better?
Measurements in Florida with a pyranometer show that the average one-year deposition of Total Ultraviolet (TUV, 295 - 385 nanometers) at 26 degrees facing south is 275MJ/m^2. If we integrate the energy deposited in a laboratory xenon-arc device for the same bandwidth with an irradiance level (light output) of the lamp set at 0.55 W/m^2/nm, it will take 1,620 hours to deposit the 275MJ/m^2 (using a Borosilicate Type S inner and outer filter). The Sunshine carbon-arc instrument will take about 1,300 hours to deposit an equivalent amount of energy. Again, these values only take into consideration the amount of light deposited on a surface in a selected bandwidth of the total spectrum, without regard for the spectral sensitivity of the material, the temperature range and amount of moisture (in any form) encountered in the different "climates", and the naturally occurring variability in the outdoor test.
I can't really decipher it but....If you can decipher this it may help. It came from here but I don't understand it
FWIW, I attended a John Wiles symposium a couple of years ago where he showed pictures of colored USE-2 wire that had been in the field for a few years which had insulation that was sunbleached and crumbling. His recommendation was to use only black.I do know colors other than black require significant additions of UV stabilizers to make them suitable for the application.
Now tell that to NEC for applications of say a grounded conductor that is smaller than 4 AWG being used at service weatherheads or similar locations.FWIW, I attended a John Wiles symposium a couple of years ago where he showed pictures of colored USE-2 wire that had been in the field for a few years which had insulation that was sunbleached and crumbling. His recommendation was to use only black.
I don't try to tell the NEC nuthin'. I just use all black USE-2 or PV wire conductors in exposed locations. I recommend the same, but it's free advice and worth every penny.Now tell that to NEC for applications of say a grounded conductor that is smaller than 4 AWG being used at service weatherheads or similar locations.