Toros
- Tujunga, CA
To calculate new panel AIc based avail. s.c, (The new panel is fed through 150kva, 480-120/208-3ph. xfrmer), can I use xfrmer's impedance and load that is 150kva @ 480v= 181A thank you
The 181 amps is the rated full load of the transforrmer, place more load on it and it will attempt to deliver that load. A short circuit is a situation where the load is much more than the transformer can deliver, that is when the actual amount of current that will flow is limited by the impedance of the transformer, in combination with the impedance of conductors between the transformer and the short circuit point, and the amount of current the supply circuit to the transformer can deliver will also have limitations. The simplest calculations assume infinite ability of the supply circuit, and basically from there you take voltage and impedance and calculate how much current would flow given those values. You do need to figure out if the transformer has say 2% impedance just exactly what kind of impedance in Ohms that means to do the simple calculation though and then it just becomes E=IxR. Someone else would be better for telling you just exactly how to determine R from the 2% impedance than me.To calculate new panel AIc based avail. s.c, (The new panel is fed through 150kva, 480-120/208-3ph. xfrmer), can I use xfrmer's impedance and load that is 150kva @ 480v= 181A thank you