I'm not real clear on your question. You seem to be implying that they are giving you a 480Y/277 service and you want to step down to 208Y/120. The POCOs primary is irrelevant to you. You would just use a standard 480 delta X 208Y/120 transformer.I'm working on a project in an area that I'm not familiar with the utility or their distribution voltage. The utility confirmed the voltage as 8320GRDY/480. So do I connect with a Wye-Wye transformer or a Delta-Wye and connect the grounds/neutrals together?
Still the same reply... just different.Sorry missed a 0 on the utility voltage. The utility voltage is 8320GRDY/4800 and I'm stepping down to 480Y/277.