boucher0331
- connecticut
Is a EMT coupling considered a tubing termination point.:slaphead:
358.30 A
			358.30 A
I am asking out of the 2011 code. I am asking because WE have a debate going on in our class right now. What year are you working from.
What would be another tubing termination example ?
Thank you again for your help. If any one has any input please speak up.
Thank you!
Thank you!
The verbiage was change in the 1993 code changing the word at the end from (fitting) to (conduit body).
314.23(E) Raceway Supported Enclosure, Without Devices,
Luminaires, or Lampholders. An enclosure that does not
contain a device(s) other than splicing devices or support a
luminaire(s), lampholder, or other equipment and is sup-
ported by entering raceways shall not exceed 1650 cm 3
(100 in. 3 ) in size. It shall have threaded entries or have
hubs identified for the purpose. It shall be supported by two
or more conduits threaded wrenchtight into the enclosure or
hubs. Each conduit shall be secured within 900 mm (3 ft) of
the enclosure, or within 450 mm (18 in.) of the enclosure if
all conduit entries are on the same side.
Exception: The following wiring methods shall be permit-
ted to support a conduit body of any size, including a con-
duit body constructed with only one conduit entry, if the
trade size of the conduit body is not larger than the largest
trade size of the conduit or tubing:
(1) Intermediate metal conduit, Type IMC
(2) Rigid metal conduit, Type RMC
(3) Rigid polyvinyl chloride conduit, Type PVC
(4) Reinforced thermosetting resin conduit, Type RTRC
(5) Electrical metallic tubing, Type EMT
In reading this I'm not so sure that I would include a conduit body on the list of termination points.
All that is saying is that the conduit can support the conduit body. IMO, you still need a strap within 3' of the conduit body as shown and the lb is a termination point. Also 358.30 includes conduit body and seems to refer to it when it states " or other terminations"
I'm not so sure but what you're saying would make sense. The way I read the exception you could have two supports 10' apart with a conduit body right in the middle providing it's the same size as the trade size of the raceway.
Luminaries, or Lampholders. An enclosure that does not
luminaire(s), lampholder, or other equipment and is supported
by entering raceways shall not exceed 1650 cm3
(100 in.3) in size. It shall have threaded entries or have hubs
identified for the purpose. It shall be supported by two or
Boxes are not permitted to be supported by rigid raceways
using locknut's and bushings. Enclosures without devices or
luminaires are considered to be adequately supported, provided
the conduit is connected to the enclosure by threaded
hubs and the threaded conduits enter the box on two or more
sides and are supported within 3 ft of the enclosure. A box is
not permitted to be supported by a single raceway.
Exception: The following wiring methods shall be permitted
to support a conduit body of any size, including a conduit
nope see in red below:
The exception does not relive the requirement of support within 3'
What does not make any sense to me is that the exception totally undoes the rule it was written under, the same goes for 314.23(F)
Second is that it was always required the raceway to be threaded into hubs built into the box or listed hubs and not by lock-nut and or bushings, I don't see where the exception makes a change to this, but it list EMT as one of the wiring methods???
Third, the exception can be applied only if the
trade size of the conduit or tubing, so EMT goes all the way up to 4" so as long as you don't have a 5" conduit body the exception is a go, so you run 1/2" EMT and install a 4" conduit body????
It does not say it has to be the same size of the conduit you ran?
Say that is true, how do you you get around the requirement to secure the conduit within 3' of a termination (assuming you agree a conduit entering a conduit body represents a conduit termination, and the securing exception to 5' is not applicable)?The heading of that section is "314.23(E) Raceway Supported Enclosure, Without Devices, Luminaries, or Lampholders." IMO the exception negates any requirement for a conduit body to have a support within 3' with the intention that the conduit body is the same size as the conduit.