Luminaire in Elevator Pit
charlie b
Lockport, IL
Retired Electrical Engineer
A client commented on a drawing package, say that since the elevator pit is sprinklered, all electrical components must be rated 4X. He went on to say that the luminaire, being a standard strip fixtgure with wire guard, did not satisfy that requirement. First of all, I don't believe NEMA ratings apply to luminaires. Secondly, I don't think the fact that an area is protected by a fire sprinkler system causes it to meet the definition of wet or damp area. Finally, the only requirement I could find was that if a luminaire is in a wet or damp area, it must be listed for that area. So I think this client is "all wet."
Comments?
Comments?
I will agree with you that an area protected by a sprinkler system is not Wet under the NEC.
Would the ground floor and basement of a building subject to flooding also be a wet area? Not in my opinion. :)
You just have to accept that there will be damage when a sprinkler is activated and using a dry or damp rated fixture in that case does not seem to me to be a particular safely hazard except to an elevator tech who is in the pit the time and started the fire. :angel:
Comments?
I think you are correct. Think about it. Is every sprinklered office area around the world now suddenly a wet or damp area? That would be a ridiculous conclusion.
Do they make a 4X smoke head? All lights I've ever seen are water resistant!
Is there a personal interest in the pit that the owner is not stating?
It just seems totally loopie!
I don't have an answer, but I do know I have been forced on the past few elevator pits to install fluorescents rated for wet locations "due to the elevator code." FWIW.
that was my first thought.... everything under a sprinkler head needs to be waterproof?
tell the customer to go soak his head... see if it meets classification.....
As George pointed out, the NEC will not be the only code in play here, so be careful what you advise the customer to do. :)
so... there is a specific section of a code preventing
me from telling a customer to go soak their head?
i had no idea. thanks... ;-)
this is distressing. i may have to quit contracting.
i just lost all my contract negotiating skills in one fell swoop.