Please take a look at the diagram below:
I want to calculation the three-phase voltage drop on each 130 ft segment. I just want to confirm from you people that would I get a reasonably accurate voltage drop if I just add up the fixture currents like this:
...then use these values in the usual three-phase voltage drop formula to find the voltage drop on each segment, and lastly add them up to get the total three phase voltage drop on the circuit?
Also, would the above method also applicable to the scenario where each fixture was connected phase to neutral, instead of phase to phase like in my example (assuming no unbalanced currents)?
Any input will be appreciated.
I want to calculation the three-phase voltage drop on each 130 ft segment. I just want to confirm from you people that would I get a reasonably accurate voltage drop if I just add up the fixture currents like this:
390 ft | 0.5 A |
260 ft | 1.0 A |
130 ft | 1.5 A |
...then use these values in the usual three-phase voltage drop formula to find the voltage drop on each segment, and lastly add them up to get the total three phase voltage drop on the circuit?
Also, would the above method also applicable to the scenario where each fixture was connected phase to neutral, instead of phase to phase like in my example (assuming no unbalanced currents)?
Any input will be appreciated.