mwm1752
Senior Member
- Location
- Aspen, Colo
Although who installed the wiring is a good clue as to the jurisdiction over the wire and more importantly where the service point is.
It sounds like the panel st the house is being treated as the service point.
If that determination is valid, then how many locations before that point the utility chooses to ground the neutral is not an NEC issue.
So, what factors might conclusively establish where the service point and the designated service disconnect is?
If any loads like A/C or outbuilding are tapped off before the breaker at the house or the feed to an internal sub panel does not go through that breaker then it is probably not the service disconnect.
Where there are ground neutral bonds is also a clue.
Tapatalk!
You are correct IMO but I have not seen the utility choose the point of demarcation after the first point of disconnect. They do not want responsibility of damaged goods from anothers install. I have never seen the utility install service equipment. But my area is limited maybe someone esle has experienced that. If the issue of installing an ECG in this instance is no more than a ownership issue, does the insinuate that the utility does not see a life safety issue in the 3 wire install?