Diaz. jesus
New member
- Miami
I found this question in a Master electrician skills test(KJ Keller)
In an eight-unit apartment building, each kitchen contains a 3.5 kw, 240 v electric range.
The demand load for the electric service to the building MUST include an ALLOWANCE for the minimum demand load of all the ranges, which would be which of the following:
a) 28 b)21 c)14 d)7.5
According to the author the answer is 21 kva Reference section 220.17 ? and list a demand factor of 0.75 for four or more appliances
28x3x0.75=21, which I think relates to 220.53 Appliance load, that specifies OTHER THAN electric ranges, clothes dryers, etc.
But according to a Mike holt example on Electrical formulas with sample calculations When using the optional calculation method , the calculated load for the appliances that are fixed in place according to T 220.84, for 8 units we should use 43 %.
Finally, When we should use T 220.55 , if for 8 ranges, 3.5 kw , Column B we should use a Demand factor of 36 %.
Please, give me some explanation about the rules I must follow in order to get it right.
Jesus
Jesus