Its a 4 wire 460 to 208/120 . It is 3phase 45 kvA transformer. I am not sure if the bond from xo should the same size as the neutral conductor. Will bond and ground in trans.
I hope this helps. Thanks for your help.
As infinity has said, the guide is T250.66 (not limited to 3/0). The neutral conductor size is not particularly relavent.
Additional references:
250.28.D.3 which takes you to
250.28.D.1 which takes you to
T250.66
Alos look at T250.66, note 2 and note a
My current practice is to size the SBJ, GEC using the xfm secondary conductor size (normally based on fla x 1.25), and T250.66. Unless for some odd reason the conductors are small, then I tend to use note 2 and size SBJ for the maximum size conductors that could be required.
ice