G gbuschling Member Location Chesapeake Beach, Md Mar 4, 2014 #1 Are branch circuits allowed to be run from a panel directly in front of a window. I think I've attached a picture.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Mar 4, 2014 #2 Does the window open?
kwired Electron manager Location NE Nebraska Occupation EC Mar 4, 2014 #3 Maybe, maybe not. I'd say depends mostly on other factors and not solely on the fact the window is there. Are they subject to physical damage? Does the window open? Does it need to open? Sunlight resistance of the cables could be an issue.
R RLyons Senior Member Location Changed for anonymity Mar 4, 2014 #4 And they put plywood to the right of the window as if to avoid such a situation :slaphead:
G GoldDigger Moderator Staff member Location Placerville, CA, USA Occupation Retired PV System Designer Mar 4, 2014 #5 The extra 100' or so of wire to route all of the circuits that way would have cost them all of their profit on the job. Tapatalk!