DBoone
Senior Member
- Location
- Mississippi
- Occupation
- General Contractor
This is a 200A meter/main on a remodel we are doing. Looking at the sticker on the cover it looks like we should land the EGC down in the bottom right corner and then land the GEC right below the service neutral, and any branch circuits originating from this service equipment we can land the neutrals and EGCs on the bar below the service neutral. Sound right?
This is the 200A GE panel inside the house that is being fed from the meter/main. I am treating it as a subpanel and removed the bar connecting the neutral buses and installed the bonding screw on the EGC bar.