External Disconnect Switch: For Listed inverters, the Company may require an
external disconnect switch (or comparable device by mutual agreement of the
Parties) at the PCC with the Company or at another mutually agreeable point that
is accessible to Company personnel at all times and that can be opened for
isolation if the switch is required. The switch shall be gang operated, have a
visible break when open, be rated to interrupt the maximum generator output and
be capable of being locked open, tagged and grounded on the Company side by
Company personnel. The visible break requirement can be met by opening the
enclosure to observe the contact separation. The Company shall have the right to
open this disconnect switch in accordance with this Interconnection Tariff.