I'm kind of stumped by a circuit that's just recently started tripping. It's been in service for five years and hadn't seen a GFCI trip until a few months ago. The gap between first and second trip was about two months but the time between gaps has been reducing exponentially.
Originally the curcuit was a 15 AMP GFCI breaker feeding four recepticals which power four stenner perastaltic pumps (about 1.9 amps each). The power to each receptacle is switched by a small automotive relay (rated for 2A inductive).
I checked continuity from hot to ground and got nothing, neutral to ground got nothing (after disconnecting the GFCI netural at the breaker), hot to netural nothing (with breaker off and everything unplugged of course). Resistance through each motor was the same as a brand new one I have on the shelf.
Electrician replaced the GFCI breaker but that made zero difference.
We then switched to a regular breaker and I installed four GFCI receptacles figuring that if it's a motor then only once receptacle would trip. It didn't even make it a day before all four receptacles were tripped.
Attached is a pic of the wiring (ground not shown due to laziness) the switches shown are actually relays.
Thinking I had a brain fault I checked and indeed all four are wired to LINE, not LOAD. I did notice a low voltage at one receptacle and when I checked the relay it appeared the contact was pretty burnt. I checked the others and they are pretty bad as well. I replaced two and on the other two I just switched to the second set of contacts which hadn't been used.
I'm thinking maybe the burnt contacts were causing the trips as these pumps aren't tripping GFCI in any other location (have six others in operation in other places) and hadn't been tripping here for several years prior to now.
Could that be the cause? Is so, what would actually cause the trips? Low voltage? (brownout) Perhaps arcing or rapid on/off from poor electrical contact? Or am I barking up the wrong electrical pole entirely?
Thanks!
Originally the curcuit was a 15 AMP GFCI breaker feeding four recepticals which power four stenner perastaltic pumps (about 1.9 amps each). The power to each receptacle is switched by a small automotive relay (rated for 2A inductive).
I checked continuity from hot to ground and got nothing, neutral to ground got nothing (after disconnecting the GFCI netural at the breaker), hot to netural nothing (with breaker off and everything unplugged of course). Resistance through each motor was the same as a brand new one I have on the shelf.
Electrician replaced the GFCI breaker but that made zero difference.
We then switched to a regular breaker and I installed four GFCI receptacles figuring that if it's a motor then only once receptacle would trip. It didn't even make it a day before all four receptacles were tripped.
Attached is a pic of the wiring (ground not shown due to laziness) the switches shown are actually relays.
Thinking I had a brain fault I checked and indeed all four are wired to LINE, not LOAD. I did notice a low voltage at one receptacle and when I checked the relay it appeared the contact was pretty burnt. I checked the others and they are pretty bad as well. I replaced two and on the other two I just switched to the second set of contacts which hadn't been used.
I'm thinking maybe the burnt contacts were causing the trips as these pumps aren't tripping GFCI in any other location (have six others in operation in other places) and hadn't been tripping here for several years prior to now.
Could that be the cause? Is so, what would actually cause the trips? Low voltage? (brownout) Perhaps arcing or rapid on/off from poor electrical contact? Or am I barking up the wrong electrical pole entirely?
Thanks!