Nutmegger
- Fairfield County, Connecticut
Residential job. The customer had his own 12/3 AC cable and wanted us to use it to wire his addition. Not sure if he's saving any money, but I don't get involved in bidding.
The boss said "yes". There are no MWBC's, and there are just two three-way switch setups, but every lighting outlet and receptacle will still be fed with a 12/3 cable, thus wasting an extra conductor in most of the circuits.
So, seeing as one of the hot conductors is getting wasted, and the steel jacket of the AC is not the best grounding conductor, I was thinking of re-designating the red as the extra grounding conductor, a la HCF MC, by marking it with green tape inside the boxes. Before my boss laughs at me, can you guys tell me if this is allowed -- re-designating ungrounded conductors as grounING ones?
And a follow-up question... Say we had 12/4 on hand (white, red, black and blue). Could we use it as 12/2/2, i.e. could we re-designate the blue as another neutral?
I know you can re-designate a grounded conductor in a cable assembly as a "hot", but want to know if a "hot" can be re-marked as a grounding or a grounded...