Anyone have any input or recommendation of a method to determine whether running 2 motors driving fans fed from 1 VFD at half speed is more efficient that running 1 motor at nameplate speed? My gut instinct is to say that running one motor at near nameplate speed is better than running 2 motors at half nameplate speed simple due to the fact that you are wasting energy creating a field in the second motor, basically the extra energy needed for the reactive power, and introducing some loses inside the VFD.
When I started digging for data for this evaluation I found that torque varies as the cube of input power for variable torque applications. So at half the torque I need 1/8th the input power. meaning that unless the motors run ALOT more inefficient at half speed then it would be much more efficient to run 2 motors at half speed from a VFD then 1 motor at nearly full speed. Based on the motor curves I have looked at the efficiency for 460V inverter duty rated motors, efficiency doesn't drop off significantly until roughly 30% or less of nameplate speed.
A few other variable I'm unsure how they effect this evaluation: how does VFD efficiency vary with respect to the motor speed (I'm assuming very little), I'm unsure what powerfactor does when you drop the speed of a motor down when it is fed from a VFD (again i'm assuming very little).
Anyone else looked at something like this? Any articles, formulas, other forum posts, and/or common sense that I can apply to this would be greatly appreciated.
When I started digging for data for this evaluation I found that torque varies as the cube of input power for variable torque applications. So at half the torque I need 1/8th the input power. meaning that unless the motors run ALOT more inefficient at half speed then it would be much more efficient to run 2 motors at half speed from a VFD then 1 motor at nearly full speed. Based on the motor curves I have looked at the efficiency for 460V inverter duty rated motors, efficiency doesn't drop off significantly until roughly 30% or less of nameplate speed.
A few other variable I'm unsure how they effect this evaluation: how does VFD efficiency vary with respect to the motor speed (I'm assuming very little), I'm unsure what powerfactor does when you drop the speed of a motor down when it is fed from a VFD (again i'm assuming very little).
Anyone else looked at something like this? Any articles, formulas, other forum posts, and/or common sense that I can apply to this would be greatly appreciated.