Another thread made me think of this question. I am assuming that raceways on a rooftop do not have to be adjusted if the raceway falls under 310.15(A)(2)-- any arguments there????
If the above is true and I have 100' run of conduit and say 10' outside to the disconnect and then 10' or less to the unit can I still use 310.15(A)(2) for the feeder to the disconnect and then have to use the adjustment factor on the run from the disconnect to the unit (RTU).? or because the run outside is 20' then the entire run must be sized with the adjustment.
MY opinion-- is the first part- bold section.
If the above is true and I have 100' run of conduit and say 10' outside to the disconnect and then 10' or less to the unit can I still use 310.15(A)(2) for the feeder to the disconnect and then have to use the adjustment factor on the run from the disconnect to the unit (RTU).? or because the run outside is 20' then the entire run must be sized with the adjustment.
MY opinion-- is the first part- bold section.