Actually that all changed.
404.9 Provisions for General-Use Snap Switches.
(B) Grounding. Snap switches, including dimmer and similar
control switches,
shall be connected to an equipment
grounding conductor and shall provide a means to connect
metal faceplates to the equipment grounding conductor,
whether or not a metal faceplate is installed. Snap switches
shall be considered to be part of an effective ground-fault
current path if either of the following conditions is met:
(1) The
switch is mounted with metal screws to a metal
box or metal cover that is connected to an equipment
grounding conductor or to a nonmetallic box with integral
means for connecting to an equipment grounding
conductor.
(2) An equipment grounding conductor or
equipment
bonding jumper is connected to an equipment grounding
termination of the snap switch.
Exception No. 1 to (B): Where
no means exists within the
snap-switch enclosure for
connecting to the equipment
grounding conductor, or where the wiring method does not
include or provide an equipment grounding conductor, a snap
switch without a connection to an equipment grounding conductor
shall be permitted for replacement purposes only. A
snap switch wired under the provisions of this exception and
located within 2.5 m (8 ft) vertically, or 1.5 m (5 ft) horizontally,
of ground or exposed grounded metal objects shall be
provided with a
faceplate of nonconducting noncombustible
material with nonmetallic attachment screws, unless the
switch mounting strap or yoke is nonmetallic or the circuit is
protected by a ground-fault circuit interrupter.
Exception No. 2 to (B): Listed kits or listed assemblies shall
not be required to be connected to an equipment grounding
conductor if all of the following conditions are met:
(1) The device is provided with a nonmetallic faceplate
that cannot be installed on any other type of device,
(2) The device does not have mounting means to accept
other configurations of faceplates,
(3) The device is equipped with a nonmetallic yoke, and
(4) All parts of the device that are accessible after installation
of the faceplate are manufactured of nonmetallic
materials.
Exception No. 3 to (B): A snap switch with integral nonmetallic
enclosure complying with 300.15(E) shall be permitted
without a connection to an equipment grounding conductor