Hi and thanks for any input on this.
I am quoting a job that will require a tap(s) (less than 10 feet) from a generator feeder to feed 2 separate ATS's.
The generator is a 60kw and the transfer switches will be 100 amp rated and 200 amp rated.
In Art. 240.21 (B) (1) (2) the requirements do not mention any OCPD as I see mentioned in
Art.21 (B) (5) (2) for taps of unlimited length.
The auto transfer switches do not have OCPD for the generator feeder, only the normal power
feeder (according to what the generator tech that I am working with that will supply the Gener**
ATS's. is telling me)
There is very limited room on this job to mount equipment and if I do not need any OCPD for the
100 amp tap (which will be less than 10 feet) I will not use it.
One other question that I had was under the tap rule for unlimited length, is it also acceptable to bring 2 separate feeders off a breaker that is rated or configured to supply 2 conductors per leg as
tap conductors? In other words a 60kw genset with a 300A breaker with double barrel lugs on each phase leg. To use this point to "tap" a 100 amp feeder and separate 200 amp feeder each going to individual main breaker load centers?
Thanks again for input as I have limited experience in using taps.
M
I am quoting a job that will require a tap(s) (less than 10 feet) from a generator feeder to feed 2 separate ATS's.
The generator is a 60kw and the transfer switches will be 100 amp rated and 200 amp rated.
In Art. 240.21 (B) (1) (2) the requirements do not mention any OCPD as I see mentioned in
Art.21 (B) (5) (2) for taps of unlimited length.
The auto transfer switches do not have OCPD for the generator feeder, only the normal power
feeder (according to what the generator tech that I am working with that will supply the Gener**
ATS's. is telling me)
There is very limited room on this job to mount equipment and if I do not need any OCPD for the
100 amp tap (which will be less than 10 feet) I will not use it.
One other question that I had was under the tap rule for unlimited length, is it also acceptable to bring 2 separate feeders off a breaker that is rated or configured to supply 2 conductors per leg as
tap conductors? In other words a 60kw genset with a 300A breaker with double barrel lugs on each phase leg. To use this point to "tap" a 100 amp feeder and separate 200 amp feeder each going to individual main breaker load centers?
Thanks again for input as I have limited experience in using taps.