Can't seem to find a clear answer to these questions RE:250.64(E)---
1) The Article states bonding of both ends of GEC installed in metal conduit or in my case as armored sheathing, at the rod end its achieved with an "armored" ground clamp but at the panel end what is the conector approved for this (around here I see everyone using a "romex" clamp which I believe is NOT listing for bonding/grounding)
I am trying to attach a photo but no sure it will work
2) When the GEC is installed in metallic---is the metal conduit/armor only required to be bonded at the can or the GEC to the metal conduit/armor (via bond bushing)?
NOTE: have looked at the NEC Illustrated and Mike Holt Illustrated and its unclear if its the bonding of the GEC or the metal/armor or both
1) The Article states bonding of both ends of GEC installed in metal conduit or in my case as armored sheathing, at the rod end its achieved with an "armored" ground clamp but at the panel end what is the conector approved for this (around here I see everyone using a "romex" clamp which I believe is NOT listing for bonding/grounding)
I am trying to attach a photo but no sure it will work
2) When the GEC is installed in metallic---is the metal conduit/armor only required to be bonded at the can or the GEC to the metal conduit/armor (via bond bushing)?
NOTE: have looked at the NEC Illustrated and Mike Holt Illustrated and its unclear if its the bonding of the GEC or the metal/armor or both