I've had a Designer I work with send me these two photos and asked if the door, not the entire panel cover, could be removed to allow a piece of art to hang correctly.

My first thought is it would be OK, no live parts are accessible.

Anyone care to chime in?
 

Attachments

  • IMG_0181.JPG
    IMG_0181.JPG
    36.8 KB · Views: 0
  • IMG_0182.jpg
    IMG_0182.jpg
    142.2 KB · Views: 0

fmtjfw

Senior Member
Nope, the door is part of the cabinet. Unless you can get a different style door from the manufacturer of the circuit breaker cabinet that is listed for the cabinet pan, you can't change it.

The fact that it would be covered by a presumably flammable art work is a really bad idea.

If the designer suggested that you leave off box covers for j-boxes or cover plates for switches would you go along?

If the designer wants to hang a piece of art work over the panel, perhaps the designer can design a spacer behind the art work that allows it to hang properly over the door.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Or as illustrated in another thread, just cover the panel with some nice wallpaper, put a frame around it and call it a work of art.

Tapatalk!
 

buzzbar

Senior Member
Location
Olympia, WA
Occupation
Electrical Contractor
Nope, the door is part of the cabinet. Unless you can get a different style door from the manufacturer of the circuit breaker cabinet that is listed for the cabinet pan, you can't change it.

The fact that it would be covered by a presumably flammable art work is a really bad idea.

If the designer suggested that you leave off box covers for j-boxes or cover plates for switches would you go along?

If the designer wants to hang a piece of art work over the panel, perhaps the designer can design a spacer behind the art work that allows it to hang properly over the door.
I disagree. You can get panels with the breaker handles exposed. They're kind of ugly, but they DO make them. It wouldn't bother me to remove the door (just the hinged portion), and hang a painting over it. But that's just, like, my opinion man.
 

Fulthrotl

~Autocorrect is My Worst Enema.~
I disagree. You can get panels with the breaker handles exposed. They're kind of ugly, but they DO make them. It wouldn't bother me to remove the door (just the hinged portion), and hang a painting over it. But that's just, like, my opinion man.

yep, and if it has a UL listing, then you are good to go.

but if it was listed with that little door on it, and you take the door off....
the listing goes away as well.
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
I don't see a problem. As stated before they make panels without a front door. You can call SQAURE-D and see if removing the door will remove the listing.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
I don't see a problem. As stated before they make panels without a front door. You can call SQAURE-D and see if removing the door will remove the listing.

The listing simply says that the item was built and shipper from the factory based on certain standards.

Just about everything you do in the field, including making conduit entries, has the ability to cause the device to no longer be in compliance with the original manufacturing standards.

According to UL it is up to the AHJ, not the manufacturer, to pass judgement on field modifications.
 

kwired

Electron manager
Location
NE Nebraska
The listing simply says that the item was built and shipper from the factory based on certain standards.

Just about everything you do in the field, including making conduit entries, has the ability to cause the device to no longer be in compliance with the original manufacturing standards.

According to UL it is up to the AHJ, not the manufacturer, to pass judgement on field modifications.

That has always been the way I see it, yet everyone gets hung up on "violating listings" in so many cases if you make any modification.

To that my reply is if you own and use KO punches or drill bits for making raceway and cable entries, you are violating a listing nearly every time you use them. Buy a cabinet with no pre-punched KO's and how are you supposed to get any wiring into it without making field modifications?
 

fmtjfw

Senior Member
That has always been the way I see it, yet everyone gets hung up on "violating listings" in so many cases if you make any modification.

To that my reply is if you own and use KO punches or drill bits for making raceway and cable entries, you are violating a listing nearly every time you use them. Buy a cabinet with no pre-punched KO's and how are you supposed to get any wiring into it without making field modifications?

Give me a break

If you buy a holeless cabinet, it is obvious to everyone -- the manufacturer, the NRTL, the inspector, and yourself -- that you must put holes in it to use it.

If you have a cabinet which has a door on it -- it is not obvious to anyone -- the manufacturer, the NRTL, the inspector, or a passerby -- that you must take the door off to use it.

APPLES and ORANGES
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
If the homeowner didn't care I would do it. Some of the smaller Siemens and QO loadcenters don't even have doors, so I wouldn't have a problem removing this one if the customer wanted it that way.
 
Last edited:

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
The point about what to do with any labelling (sometimes pretty extensive) attached to the inside of the door still concerns me. Make a photocopy of it and insert in an envelope inside the panel?

Tapatalk!
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I'm happy when I find panels of that era behind paintings and they even have covers much less doors :D
 

Smart $

Esteemed Member
Location
Ohio
I've had a Designer I work with send me these two photos and asked if the door, not the entire panel cover, could be removed to allow a piece of art to hang correctly.
My first thought is to just use stand-off hanging techniques. IMO, artwork spaced out from a wall surface yields better viewing aesthetics.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The enclosure and cover for the panelboard are not required to be listed products. Those items are covered by Article 312.
 