ohmhead
Senior Member
- Location
- ORLANDO FLA
Question we have a factory water pump unit it has three motors 7.5 hp each the nameplate on unit shows 37.5 fla total load this is a 480 v 3ph packaged unit .
The nameplate shows a 60 A required breaker. Can I put this on a 45 amp breaker in panel if UL listed for 100% operation in encloser .
If the unit has a duty cycle possible or can a 45 amp breaker be rated at 100 % possible what could be a rule or what might be a way to use that 45 amp breaker in this case .
Breaker rated at 80 % or 100% does the code state this what article ?
My wire size to this unit is 6 copper with 8 ground .
The nameplate shows a 60 A required breaker. Can I put this on a 45 amp breaker in panel if UL listed for 100% operation in encloser .
If the unit has a duty cycle possible or can a 45 amp breaker be rated at 100 % possible what could be a rule or what might be a way to use that 45 amp breaker in this case .
Breaker rated at 80 % or 100% does the code state this what article ?
My wire size to this unit is 6 copper with 8 ground .