Two 100 amps

Status
Not open for further replies.

domnic

Senior Member
Occupation
Electrical Contractor
I want to install a two gang 100 amp meter base with disconnects for each can I run the feeder wires in the same conduit in to the building ? what code article ?
 
If the disconnects are outside with the meters, then the downstream circuits are feeders, not services. You just have to remember to derate for multiple current-carrying conductors.
 
Are you dealing with multiple occupancies?

May not be acceptable in some of those instances to feed one occupant through another occupant space.

If you have a single occupancy with multiple meters there shouldn't be any problem.
 