EGC
domnic
Electrical Contractor
Wen I have a 200 amp meter base with built in 200 amp breaker disconnect must I rum a EGC to the 200 amp panel ? ( service for home)
Yes, the conductors between the service disconnect and the panel are feeder conductors and they require an EGC to be run with the feeder. On the line side of the SD no EGC used as it would create a parallel path for the neutral current.
If you wish you can use your metallic conduit as the EGC.
EGC
If I use the conduit for ECG I would bond the conduit to the grounding bar not the neutral bar?
The fact that the conduit is fastened to the panel as well as the equipment grounding bar will suffice but if you desired additional bonding such as a bond bushing it is certainly allowed. The primary thing to remember is that there can be no grounded (neutral) to grounding connections after the service (1st) disconnect as noted in 250.24(A)(5) (and exceptions)