I want to install 9 sets of a 3-wire+neutral feed in a 9-conduit ductbank (3x3). It's a 3,000 amp, 480Y/277V feed.
Figure B.310.2 shows this configuration, but Table B.310.5, the only table to refer to Figure B.310.2, calls out one conductor per conduit.
I will be using a 0.8 factor for more than 3 CCC's, and a soil impedance rho of 0.9, but I'm at a loss on calculating the derating factor for ambient temperature, since it doesn't seem to fit the table.
Any help is greatly appreciated.