230/130 volts

Status
Not open for further replies.

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)
Seems like a no brainer bu can I use a 240v disconnect for 130/230 volt equipment?

I don't have any help, cause I'm not familiar with 130/230V systems. But I am curious. Is this a Wye connected system, 130V line to neutral, 230V line to line?

If so:
Is the 240V disconnect you are looking at a 3 pole for a piece of 3phase equipment?
Does the utilization equipment need a neutral?
Is the neutral grounded?​

Just curiousity - I always like to learn new things. I've seen 240/139V grounded Wye, 3 phase. Used where 3 phase 240V is needed and the equipment mfg does not like 240V Delta. But I am not familiar with 130/230V.

ice
 

kwired

Electron manager
Location
NE Nebraska
I don't have any help, cause I'm not familiar with 130/230V systems. But I am curious. Is this a Wye connected system, 130V line to neutral, 230V line to line?

If so:
Is the 240V disconnect you are looking at a 3 pole for a piece of 3phase equipment?
Does the utilization equipment need a neutral?
Is the neutral grounded?​

Just curiousity - I always like to learn new things. I've seen 240/139V grounded Wye, 3 phase. Used where 3 phase 240V is needed and the equipment mfg does not like 240V Delta. But I am not familiar with 130/230V.

ice
If it were a wye system with 230 volts phase to phase the voltage to neutral would be just shy of 133 volts.
 

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)