DBoone
- Mississippi
- General Contractor
You need to replace all the light fixtures in a house that has old 60C NM. Fixtures require minimum 90C conductors.
Or you can pigtail the original wiring with higher temp conductors at the ends. It might require an additional box to get spacing.
Tapatalk!
I have pulled down old fixtures and had the insulation from the old wires turn to dust in my hands.
On the other hand I have seen lots of old, old wiring still in service...... soldered connections insulated with friction tape, crimps and diaper wraps, boxes crammed fuller than a can of worms you take fishing. I marvel at how those old guy did it.
Do what you need to do. If you have only done new work, get two of your best electrician friends to look at it with you. If you have done service work for a while, do what your gut tells you.
Problem always seems to be the ceiling outlet box is a common point for many cables, and box fill didn't seem to be anything important 30-40+ years ago.If there an attic as others have mentioned but the cable back and install a JB with a 90? C cable to the fixture. If not then you may need to be more creative. In the past with ceiling that no access from above we have cut in boxes a few inches away from the fixture box with a blank cover for the transition and used a medallion to cover the transition box. Or just run a new cable from the switch if the feed originates there and patch the damage.
I lost track a very long time ago of how many 3.5 inch pancake boxes I have seen with 3 or 4 NM cables entering them.
With the deteriorating insulation I'll strip off some good insulation and sleeve it over the bare old wire and use marine heat shrink tube to hopefully secure the fix to what is left of the existing insulation.
Theoretical... Hypothetical...My theoretical has become a reality. Remodeling my folks house... New paint, doors, trim and floor covering in 3/4 of the house. Will be changing 3 fixtures. Do all new fixtures require 90C supply conductors or are there some put there that do not? I don't like the idea of having to put a bunch of junction boxes in the attic.