fredericktex
- Concord, CA
This subject has been broached many times, but I think I may have a unique scenario that hasn't been addressed here before.
I work for a utility company in the natural gas side of the house. We have RTU (Remote Terminal Unit) cabinets that are classified as C1D2, Group D. The cabinet's innards consist of SCADA electronics, TBs, power supply, UPS, batteries, Rosemount transmitters and various hand switches and breakers. We currently use Phoenix contact disconnectable fuse blocks with glass fuses in the XMTR circuit. This is to primarily prevent the SCADA electronics from experiencing a current overload if the hot wire is accidentally shorted to ground during maintenance. Such a condition would ruin the SCADA pack and since it has no internal fuses and is single-ended, it would have to be replaced. No salvage is possible as I understand it. No moving to a spare input, nothing.
Now, we are not in a classified area. The inside of the RTU is the classified area because there are pilot regulator vents and instrument tubing inside the cabinet with ranges anywhere from 60 - 600 PSI. The RTU enclosures are vented to the atmospehe and installed on street corners all over CA.
Here's the question: Can we use glass fuses because this is a nonincendive circuit and we also have the main AC disconnect as well as a DC breaker to remove power to all the instruments at once, not one at a time? It seems like we should be fine by my interpretation of the code, but I would like a more experienced person's input.
I feel this is a unique question because all other threads seem to be concerned with an enclosure itself inside a classified area.