I have to feed some external sub-metering equipment from our 480 gear. I need a 3 pole 30 amp feed to this equipment. It has to be feed from this gear because the current readings and voltage must be from the same source. I have no available space for a small breaker and the gear is full.

I want to make a tap inside the gear to feed this equipment off the 2000 amp bus. Applying the 10' tap rule and using a tap conductor with 1/10 the ampacity would make a really big tap conductor for a 30 amp feed. If I fuse the TAP conductor before it leaves the gear am I still required to use that large of a conductor?
 

Canton

Senior Member
Location
Virginia
Occupation
Electrician
Looks like everyones asleep. So, IMHO a 30A conductor is appropriate after a 30A fuse. It is no longer a tap. Just watch out for fill and listing violations. Good luck.

Its the tap that I am questioning. The size of the conductor to the gear's buss? If I fuse the tap before it leaves the gear am I required to size it for 1/10 the ampacity of the buss (2000amps/200amps)? 200 Amp conductor is huge for only needing a 30 amp feed. I was thinking if it were fused before leaving the gear i could use 10 to the gears buss;
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I agree, the 1/10 is for conductors that "leave the enclosure", however, in regard to your fuses, keep 240.40 in mind.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Is this 2000 amp gear service equipment? If so line side taps wouldn't have to comply with the tap rules in Article 240.
 

Canton

Senior Member
Location
Virginia
Occupation
Electrician
Is this 2000 amp gear service equipment? If so line side taps wouldn't have to comply with the tap rules in Article 240.

Hey Rob, thanks for the info. Yes it is service equipment, but we are doing the tap on the load side. I was not sure if the tap had to follow the requirements if it did not leave the gear. We are going to put a pullable fuse block in one of the cabinets.
 

kwired

Electron manager
Location
NE Nebraska
Hey Rob, thanks for the info. Yes it is service equipment, but we are doing the tap on the load side. I was not sure if the tap had to follow the requirements if it did not leave the gear. We are going to put a pullable fuse block in one of the cabinets.
Consider what kind of arc flash hazard there may be if changing these fuses as well.
 