According to NEC Table 450.3(B), for more than 9 amps for primary and secondary protection; the primary protection max is 250% and the secondary protection is sized at 125% max of the transformer rated current.
Is there any issue sizing both the primary and secondary at 125%? When doing renovation projects sometimes we try to reuse the existing conduits and wiring to save money. So the primary side might end up being only 125%.
Is there a rule of thumb that if you size the secondary at 125% the primary should be at least XXX%? Understand that there are different types of breakers and many breakers you can adjust the trip curves.
Any help would be appreciated.