Service calculation load for 8 Air handlers . 480 volt 3ph. Name plate pic. attached

Status
Not open for further replies.
Do we assume no heat load, or do we note a violation of 110.3(B) and 424.28 for not marking the nameplate ?
 
That is true, they didn't mark the name plate, but this unit has 5KW heat strips. Customer may want to use one of the larger options of heat strips listed on the name plate. Does this help? I would like to know load demand for the worse case scenario.
 
I calculated it by multiplying the MCA for the 15kw heat strips X 8 for the number of units. Then 25% of the largest rated motor, which in this case I used the compressor motor. Is this correct?
 
I calculated it by multiplying the MCA for the 15kw heat strips X 8 for the number of units. Then 25% of the largest rated motor, which in this case I used the compressor motor. Is this correct?

I think I would take the full load amps of each unit (6+0.5+3+18 = 27.5) times 8 units, and the add 25% of the largest motor.

27.5 * 8 + 1.5 = 221.5A

(I think the 208/230V listed for the indoor fan is a typo.)
 
This may have some interesting discussion.
Since you mentioned "service calculation", I would think our guide would be 220.14 which it seems would have you use the ampere rating of the load.
220.14(c) would have you add 25% to the largest motor load.
I don't see clarity as to which number to use for the heat load. IMO, the actual FLA would be the one used for service calculations.
My numbers would be same as david's in post #6 (he posted as I was typing)
 
I think I would take the full load amps of each unit (6+0.5+3+18 = 27.5) times 8 units, and the add 25% of the largest motor.

27.5 * 8 + 1.5 = 221.5A

(I think the 208/230V listed for the indoor fan is a typo.)

I agree although my math is a bit different:

6 x 1.25 (for largest motor) + 3 + 5 +.5 +18 (heater) = 30.5

30.5 x 8 = 244A ~ 250A service.

Thoughts?
 
I agree although my math is a bit different:

6 x 1.25 (for largest motor) + 3 + 5 +.5 +18 (heater) = 30.5

30.5 x 8 = 244A ~ 250A service.

Thoughts?

I don't see the need to use the 1.25 except for one (the largest) motor.
 
I agree with Gus, only need to use the 1.25 once.

I don't see the need to use the 1.25 except for one (the largest) motor.


I'm not sure how you arrived at your answer, though...6 x 1.25 (for largest motor) + 3 + 5 +.5 +18 (heater) = 34 (not 30.5).


I agree although my math is a bit different:

6 x 1.25 (for largest motor) + 3 + 5 +.5 +18 (heater) = 30.5

30.5 x 8 = 244A ~ 250A service.

Thoughts?

Also, I'm not sure where the "5" is coming from in your calculation.


 
So then my numbers would changed to...

(6 x 1.25) + 3 + 5 +.5 + 18 = 34A (math was wrong first time)

+

7 x (6 + 3 + 5 +.5 +18) = 227.5A+ 34A = 261A
 
I agree with Gus, only need to use the 1.25 once.




I'm not sure how you arrived at your answer, though...6 x 1.25 (for largest motor) + 3 + 5 +.5 +18 (heater) = 34 (not 30.5).




Also, I'm not sure where the "5" is coming from in your calculation.




You are correct... no extra 5. :roll:
 
Thanks guys! I calculated MCA which would include all the motors and heaters 33.5 x 8 x 480 x 1.73 = 222,547 va

Then for the largest motor I calculated using the compressor 6 x 1.25 x 480 x 1.73 = 6228

Add the two together 222,547 + 6228 = 228,775 va

228,775 / 480 x 1.73 = 275 amp.

What do you guys think?
 
Thanks guys! I calculated MCA which would include all the motors and heaters 33.5 x 8 x 480 x 1.73 = 222,547 va

Then for the largest motor I calculated using the compressor 6 x 1.25 x 480 x 1.73 = 6228

Add the two together 222,547 + 6228 = 228,775 va

228,775 / 480 x 1.73 = 275 amp.

What do you guys think?

((6+0.5+3+18) * 8) + (6 *0.25) = 221.5A is your load.

You don't need to use the MCA of each unit, just the FLA. (27.5*8*480*1.732=182,905VA)

And for the largest motor, you would want to add 25%, you added 125%. (6*0.25*480*1.732=1247VA)

(182,905VA + 1247VA = 184,152 VA = 221.5A @ 480V-3ph)
 
Last edited:
"what do you guys think ?"
??
david showed what he thought twice and I agreed with him.
I see nothing in service calculations that requires you to use MCA.

If you like 275.5 use it.
Do you need to use that number.. not in our opinion.

but

The Code is minimum required.
Your number is great unless someone is bidding against you and uses the required number and you loose the job.
 
((6+0.5+3+18) * 8) + (6 *0.25) = 221.5A is your load.

You don't need to use the MCA of each unit, just the FLA. (27.5*8*480*1.732=182,905VA)

And for the largest motor, you would want to add 25%, you added 125%. (6*0.25*480*1.732=1247VA)

(182,905VA + 1247VA = 184,152 VA = 221.5A @ 480V-3ph)



Thank you very much David. You are sure about this?

What is the extra amperage for in the MCA to get to 33.5 from 27.5?
 
"what do you guys think ?"
??
david showed what he thought twice and I agreed with him.
I see nothing in service calculations that requires you to use MCA.

If you like 275.5 use it.
Do you need to use that number.. not in our opinion.

but

The Code is minimum required.
Your number is great unless someone is bidding against you and uses the required number and you loose the job.

You are right Augie about competitor bidding, but I am more concerned about having enough in the service to handle the load on the building and just wanted some other opinions. You guys are great. Thanks for your time.
 