Can high rise loadcenters be tapped (in the gutter) and be Main Lugs Only if the tap conductors are greater than 33% of the riser conductors?
Rob:
Correct me, but as far as tap rules go, would 240.21(B)(1) not allow such ? 408.36 would prevent one from doing so.
Just for my education would if be legal under the 10ft tap rule if it were not for 408.36 ?
Rob:
Just for my education would if be legal under the 10ft tap rule if it were not for 408.36 ?