Anyway after I wired the house the homeowner showed up and claimed he did a ohms test on the ufer ground and it came back at 800 ohms. I'm not sure what he did to test it but I wouldn't think that could be correct.
OK this raises Red Flags. To accurately measure Ground Electrode Impedance takes some very specialized and expensive test equipment and training to use. I highly doubt the HO has the equipment or knowledge to use it. Heck not many electricians or engineers know how to do it correctly. Don't take offense guys, just stating the facts.
Second thing is for a UFER ground it is almost impossible to use a 3-point dead fall potential test using a meggar. For a 3-point test to be accurate 3 criteria has to met to be valid.
1. The test field needs to be a minimum of 8 times large than the area being tested.
2. The test line cannot pass over any metallic buried objects like a water or sewer line.
3. Must be made from multiple directions.
So for example let's say the foundation is 30 feet by 30 feet. Your test line then has to be a minimum of 240 feet. In a urban environment it would be almost impossible to meet those conditions. Only way to really do it and get somewhat accurate would require a Clamp-On loop tester and those cost $1700 for a decent one.
Even if 800 Ohms is correct, so what? It means nothing.