jaggedben
Senior Member
- Location
- Northern California
- Occupation
- Solar and Energy Storage Installer
In the past week I have failed three inspections and I feel like the major AHJ I work with has floated off into the deep end...
As a check on my sanity, I would like to ask folks here if they agree or disagree with the following statements:
1) Installing a circuit breaker for an isolated utility-interactive inverter (i.e. inverter with a transformer) into a distribution subpanel with other OCPDs presents no inherent safety danger or code compliance problem, including objectionable current.
2) A DC GEC for a utility-interactive inverter may be run through a subpanel without inherently creating a danger or code violation.
3) A combined GEC/EGC, as allowed by 690.47(C)(3) in the 2011 NEC, may be run through any number of subpanels or other enclosures to where it connects to the Grounding Electrode system, without inherently creating a danger or code violation.
4) An EGC for a subpanel may be used as an continuation or extension of a combined EGC/GEC for a utility-interactive inverter, so long as it complies with the provisions of 690.47(C)(3).
5) The presence of a transformer in a utility interactive inverter has no relevance to the safety or code compliance of a) the installation of the inverter output OCPD or b) the routing or manor of installation of a DC GEC, if required.
Assume that all inverter equipment is listed, that installations of GECs comply with the letter or 250.64, etc.
As a check on my sanity, I would like to ask folks here if they agree or disagree with the following statements:
1) Installing a circuit breaker for an isolated utility-interactive inverter (i.e. inverter with a transformer) into a distribution subpanel with other OCPDs presents no inherent safety danger or code compliance problem, including objectionable current.
2) A DC GEC for a utility-interactive inverter may be run through a subpanel without inherently creating a danger or code violation.
3) A combined GEC/EGC, as allowed by 690.47(C)(3) in the 2011 NEC, may be run through any number of subpanels or other enclosures to where it connects to the Grounding Electrode system, without inherently creating a danger or code violation.
4) An EGC for a subpanel may be used as an continuation or extension of a combined EGC/GEC for a utility-interactive inverter, so long as it complies with the provisions of 690.47(C)(3).
5) The presence of a transformer in a utility interactive inverter has no relevance to the safety or code compliance of a) the installation of the inverter output OCPD or b) the routing or manor of installation of a DC GEC, if required.
Assume that all inverter equipment is listed, that installations of GECs comply with the letter or 250.64, etc.