Was asked to look at baptistry heater that is not working. 6 KW 240 inline heater. an elder at the church said he went to turn the t/stat up and got a good shock when he touched the heater control box and a copper cold water line. So I go check it, I placed one lead of my meter to the housing of the heater and the other to the cold water line 123 volts. check heater element shorted to housing. do some checking and the equipment ground wire not connected in the control box. also the copper piping on each end of the housing to the pump and the baptistry is isolated at each end by way of connection to pvc. I know I need to connect the equipment ground wire. do I need to bond the isolated portion of the copper piping to the near by cold water copper piping and bond it also to a near by grounding electrode conductor? and why do you think the gfci did not trip when the elder got shocked? would the GFCI breaker tripped if the equipment ground wire was attached?