parallel 750 mcm Al

Status
Not open for further replies.

beanland

Senior Member
Location
Vancouver, WA
Same Insulation Type

Same Insulation Type

2011 NEC 310.10(H)(2)(4) states "Have the same insulation type" but it does not state anything more. If the insulation of all wires is thermoset, it is all the same type. If it is thermoplastic, it is all the same type. I do not think the NEC intended that if you have XHHW you cannot use XHHW-2 in parallel (limited by the lesser conditions of use). Same for THHW and THW. As long as the least conditions of use and temperature rating is applied to ALL conductors, no conductor will be operated out of its rating.
 