jgat
- United States
Hi,
I am a newbie here. We are connecting two explosion proof enclosures according to the (NEC 501.15 (A.3)) referred below. The question I have is - I can find elbows, unions and other fittings that are rated and certified for class 1 Div 1. I also need a male to male straight conduit nipple as part of the connection. However, there are no conduit nipples that are certified for class 1 div 1.
Why is this the case? Can I buy a pipe nipple from Lowes and use it with the other HazLoc certified fittings? If the threading on the conduit nipple is not made according to certain standard, how can it be guaranteed to withstand explosion? So, I doubt I can use a random metal conduit nipple. Can someone please clarify?
Best Regards,
Jgat
(501.15(A.3)) Two or More Explosionproof Enclosures. Where two or more explosionproof enclosures for which conduit seals are required under 501.15(A)(1) are connected by nipples or by runs of conduit not more than 900 mm (36 in.) long, a single conduit seal in each such nipple connection or run of conduit shall be considered sufficient if located not more than 450 mm (18 in.) from either enclosure.
Best Regards,
Jgat