A contractor has applied for a permit to add two 50 amp circuits to a house for two EVSEs. The service is 200 amps. We asked for whole-house calculations to confirm that the main panel will handle it. The contractor came back with calculations using the alternative method (220 part IV), with general loads at 100% of first 10kva, remainder of general at 40%, and HVAC at 100%. With these calcs, with the EVSE considered a general load, they just squeek by, but it's the demand factor that gives them that. So, if they plug in both cars at once while about 14000 watts of AC are operating, They could be pulling about 130 amps just through cars and AC alone (cars 35 amps each, AC about 60 amps).
Questions:
1-Is an EVSE, and/or an electric car, an 'appliance'? I say it is, based on definitions of 'appliance' and 'utilization equipment' in Art. 100
2-Can an EVSE and/or an electric car be included in 'General Loads' per 220.82(B)(3)a. which reads- 'All appliances that are fastened in place, permanently connected, or located to be on a specific circuit'? EVSEs are fastened in place but cars are not, EVSEs are permanently connected but cars are not. But- EVSEs and cars are BOTH 'located to be on a specific circuit'.
Thoughts?
Questions:
1-Is an EVSE, and/or an electric car, an 'appliance'? I say it is, based on definitions of 'appliance' and 'utilization equipment' in Art. 100
2-Can an EVSE and/or an electric car be included in 'General Loads' per 220.82(B)(3)a. which reads- 'All appliances that are fastened in place, permanently connected, or located to be on a specific circuit'? EVSEs are fastened in place but cars are not, EVSEs are permanently connected but cars are not. But- EVSEs and cars are BOTH 'located to be on a specific circuit'.
Thoughts?