Pulling a low voltage cable with 277v wires in conduit

Status
Not open for further replies.

zappy

Senior Member
Location
CA.
Cable is for lighting control panel. The cable doesnt say the voltage rating on it. So is this not code? Thank you for your help.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
If there is no voltage rating on the control cable you cannot treat it as Class 1 and apply the exception to allow it to run in the same raceway with power circuits.
Period, IMHO.

Tapatalk!
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Even if the cable were rated to be installed with the power conductors the Class 2 power supply for the lighting control panel would have to allow Class 1 re-classification before you could install them in the same raceway. We see this quite often with Lutron equipment where the control is Class 2 but is permitted to be re-classified as Class 1.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
:thumbsup:
Which in turn triggers the requirement for the rest of the circuit to follow Class 1 rules.
In the case of Lutron, this means that they have certified their loads (controls and devices) to be safe with a Class 1 power source even though they "ship" with a Class 2 power source.

Tapatalk!
 