Section 705.31 ?Location of Overcurrent Protection?
This new section limits the length of unprotected conductors in supply-side interconnections to 10 feet, due to safety concerns. According to a substantiation provided by CMP No. 4 in the ROP: ?Often, when connections are made to, or ahead of, existing service-entrance equipment, space limitations do not allow for a disconnecting means with overcurrent protection to be adjacent to the service entrance equipment and still have proper working clearances. Consequently, many of the required disconnects with overcurrent protection are being installed remote from the service entrance equipment.?
Though subject to fault current from the utility, these conductors are not protected by the utility transformer?s primary OCPD(s). The CMP concludes: ?A fault on these conductors will likely result in a violent, explosive conductor vaporization and potential equipment damage or complete burn down.? The unanimous decision to limit the unprotected conductor length to 10 feet mitigates this safety hazard.
Where the overcurrent protection for the parallel power production equipment is located more than 10 feet from the point of connection, an exception allows the use of cable limiters to provide short-circuit protection. Note that these cable limiters must be installed ?at the point where the electric power production conductors are connected to the service.? A cable limiter is different than a fuse in that it isolates a conductor in response to short-circuit current only and does not provide overload protection. Due to space constraints, it may prove easier to install cable limiters at a service entrance in accordance with this exception rather than install a fused disconnecting means within 10 feet.
The addition of Section 705.31 brings the guidance for PV supply-side connections into closer agreement with requirements in Article 230 pertaining to service disconnecting means. For example, Section 230.70(A) requires that service disconnecting means be located at ?a readily accessible location outside of a building or inside nearest the point of entrance of the service conductors.? Section 230.91 further requires that overcurrent protection be integral to or immediately adjacent to the service disconnecting means. Note that where disconnecting means for PV power production sources are located within 10 feet of the main service disconnecting means, they could be used, in conjunction with contactor combiners or other equipment, to initiate rapid shutdown for PV systems on buildings.