In example D1(b) One-Family Dwelling, Informative Annex D Examples NEC, the calculated service rating = 110A Ungrounded and 84A Grounded. However, if I do the calculation using VA instead of Amperes, I would get a service rating = 101A Ungrounded and 77A Grounded . Why was the calculation in Example D1(b) done that way using Amperes a table format instead of the way I did it below?
Example D1(b) calculated using VA
Ungrounded Conductors
Amperes from Example D1(a) = 18720 VA
One 230-V air conditioner = 1440 VA
One 115-V air conditioner = 1440 VA
One 120-V dishwasher = 1200 VA
One 115-V disposer = 960 VA
25% of largest motor (see 430.24) (1200 x 0.25) = 360 VA
= 24120 VA
24120VA / 240V = 101A
Grounded Conductor
Amperes from Example D1(a) = 14550 VA
One 115-V air conditioner = 1440 VA
One 120-V dishwasher = 1200 VA
One 115-V disposer = 960 VA
25% of largest motor (see 430.24) (1440 x 0.25) = 360 VA
= 18510 VA
18510VA / 240V = 77A
Example D1(b) calculated using VA
Ungrounded Conductors
Amperes from Example D1(a) = 18720 VA
One 230-V air conditioner = 1440 VA
One 115-V air conditioner = 1440 VA
One 120-V dishwasher = 1200 VA
One 115-V disposer = 960 VA
25% of largest motor (see 430.24) (1200 x 0.25) = 360 VA
= 24120 VA
24120VA / 240V = 101A
Grounded Conductor
Amperes from Example D1(a) = 14550 VA
One 115-V air conditioner = 1440 VA
One 120-V dishwasher = 1200 VA
One 115-V disposer = 960 VA
25% of largest motor (see 430.24) (1440 x 0.25) = 360 VA
= 18510 VA
18510VA / 240V = 77A