Withoput the proper markings including UL number any inspector would be well within their authority to reject it. If it were me I would strip it and sell it.
From that we can say after the original install it is no longer listed. And I have no problem with saying it either as same goes for many other things, once you put them to use they very well may not be in same condition as they were in when they fully met the listing requirements listing IMO only means something for new and unused products. Now it is still a good thing to have a product that was listed when it was new.An authorized use of the UL mark is the manufacturer's declaration that the product was ORIGINALLY manufactured in accordance with the applicable requirements when it was shipped from the factory. When the product is modified, in this case installed and uninstalled, UL has no way to determine if the product continues to comply with UL standards.
I demoed out a couple thousand feet of #2 thw CU There are no AWG markings only shows #2 THW is there any code against reusing this wire. Would an inspector have issues with no AWG
Many are happy with used equipment - as long as it doesn't come with a new price tag.Make some calls, find which scrap yard is paying the most and scrap it.
If you were a customer would you be happy if you got used equipment?
This is accurate. The quality control is done at the manufacturing facility. Installing in accordance with the manufacturers requirements does not remove the UL listing of a product. When you actually modify the product is when the UL listing no longer applies. For example, if you have a control panel and install a terminal block with no wires connected to it, while benign, you have still modified the panel and the UL Listing TECHNICALLY no longer applies. A UL representative would need to do an inspection of the modified panel to relist the panel. A representative of the panel builder could not do this inspection to relist. It has to be UL (and you have to pay them for it too!).
As mentioned by petersonra, if this is contract work, there is a 99.99% chance there are provisions in the specifications calling for all new products to be provided.
kwired:
Meggering is usually required by specifications to ensure that the insulation was not significantly damaged during a pull. Electricians manning tuggers usually don't concern themselves with pulling tension calculations and the like. If you are an electrician that does concern yourself with that, then kudos for doing the right thing. This old cable will certainly perform less than new cable as far as a megger test, what if you pull the cable and the test results are not satisfactory? Do you attribute it to cable age or a pull gone wrong or both?
If it was me, I would scrap it and install new cable. The owner is paying for it, so if you are going to reuse old cable he will likely want a kickback. You might make another $100 in markups... but at what cost? The owner will still hold you accountable if something does go wrong. I don't see how an AHJ could be forced to accept a reused cable that has been pulled three times (1st install, removal, 2nd install). Then you'll be replacing cable at your cost!
I pretty much agree with what you said and also agree new conductors is often the way to go. I don't see how an AHJ can be forced to accept or reject a cable that has been used if it is otherwise in good condition or with local amendments stating otherwise.