mbrooke
Batteries Included
- United States
- Technician
How does one calculate unbalanced amperage on single phase loads connected in delta (phase to phase)?
Even if the power factors match, you still have to do it by vector sum... except if they have the same magnitude. Then it's simply arithmetic sum of magnitudes times 0.866 (or one magnitude times square root of three). This arithmetic method will yield a decent approximation for unbalanced loads.You do the vector sums for each phase wire, unless all of the loads have the same displacement power factor.
If the power factors all match, then there is a formula which was recently posted here. (By iwire?)
Tapatalk!
Nope. I could explain, but I'm sure you'll figure it out for yourself.Actually, if the displacements match but magnitudes are not equal, the fact that the relative angles are all fixed at 120 degrees allows a closed form formula involving just the three magnitudes.
Similar to the formula for the neutral current in an unbalanced wye, I think.
The way I see it if all loads are purely resistive and all even such as electric heat (25kw L1-L2 25kw L2-L3 25kw L3-L1) you just multiply the current by the square root of the to give you the phase current. 25kw/240 volts= 104 amps multiplied by srt3 (104x1.73) giving you 180. 180 amps per phase and 75 kw of load. Corrrect?
Well, you got the right answer, but technically instead of multiplying by sqrt3, you should have multiplied by (sqrt3)/2 and than multiplied by 2. :angel:
... However iffy on non balanced loads such as 20kw/25kw/32kw or power factors outside of unity.
Easiest way - present all your data here and let the math geeks find the answer for you :happyyes:How does one calculate unbalanced amperage on single phase loads connected in delta (phase to phase)?
Yes. It is vector algebra.
Here is an example for delta leg currents of 1A, 2A, 3A, resistive loads, leg currents in-phase with leg voltages. So the leg currents are 3A<0, 2A<120, 1A<-120. ("<" means angle)
It looks messy, but if your calculator can do polar-rectangular swaps (and complex math) it is pretty easy. Otherwise you got to do some trig
Each one of the calcs involves:
1. swap each current vector from polar to rectangular.
2. subtract
3.swap result back to polar
If the loads are not resistive it isn't really more messy - just have to have the leg voltage to leg current displacement so you can get the current phase angle
Hope I helped and didn't just muddle
ice
That is a completely different question than the phase currents. If you are looking at straight resistive loads, it is pretty simple. Figure out the load in each delta leg, add them together - no vectors involved. The number you get is the kw the power company will charge for, or the power required from an engine to turn a generator - but not a number that you could use to size a transformer, nor use to size a generator..... Anyone know of any online software that calculate unbalanced 3 phase power?
If you are looking for complex power - I don't know what to tell you. I've never even seen an application where unbalanced 3ph power was used to do any design calculations. For example, I don't know how one would use the number for power factor.
Interesting idea - certainly something one could calculate. But I don't know what it would mean.
ice
By unbalanced 3 phase current (added by ice) I mean single phase loads that are not equal to each other in kw (current draw) connected across each leg. That would result in each leg having a different current when measured with an amp clamp or current measuring CT.
If say load connected across phase A to phase B draws 40 amps, load connected across Phase B and Phase C draws 30 amps and Load between phase C and Phase A draws 20 amps how does one mathematically calculate the current that would appear on each phase leg? This is what I meant by unbalanced current (added by ice), since the loads on each leg relative to one another are not equal.
Two issues mentioned in this thread:
Post 1
Calculate curent in each phase when each delta leg has a different load. I gave you an example of how to calculate this in post 10. It is a complex math (vector algebra) calculation even if the loads are resistive.
This is the part I need help with. Just a guided explanation.
I found this online, supposedly it does the computations automatically for current but I question its accuracy. Try it out and you'll see what I mean, but if its accurate it will help. http://www.google.com/url?sa=t&rct=...74GgDg&usg=AFQjCNGWd_ggmFPrgM7X-DSeeNlpdhvH1A
Post 12
You asked for calculation of unbalanced 3phase power - way different thing than the current. I gave the best answer I could. This one is difficult because I don't know where one would or could use the number.
I was (and still am) pretty sure the one you want is the un-balanced current - the current in each phase as noted in post 1. If the attachment I gave in post 10 didn't make any sense, that's because I didn't explain it very well. Sometimes I'm prone to that. If that is the one you are after, I should be able to do better.
ice
Couldn't get it to function. Get message about protection doesn't allow changes.I found this online, supposedly it does the computations automatically for current but I question its accuracy. Try it out and you'll see what I mean, but if its accurate it will help. http://www.google.com/url?sa=t&rct=j...-DSeeNlpdhvH1A
Yeah - that happens to me sometimes in power analysis. (color me minorly embarassed)By 3 phase power I meant the system as a to be analyzed for current. Im still referring to the first post. I didn't know you would get caught up over a single word.
My turn.... (color me minorly embarassed) ...
... I tried three different delta currents. The line currents came up fine. ...
I think you picked a good one. The shortcomings don't look important. The sheet is protected so I can't see the algolrithm. I tried three different delta currents. The line currents came up fine. The sheet assumes the loads are resistive - no phase angle information.