I was hoping someone could help me understand ATS withstand ratings when looking a the manufacturers datasheet. In looking at one particular datasheet I see there are two diferent withstand ratings given when used with "any manufacturers breakers". One rating is a 3-cycle rating at 50kA and the other rating is a 18-cycle rating at 36kA.
I'm trying to determine which of the two ratings to use for this ATS for the purposes of equipment evaluaiton. Do you have to look at the upstream breaker and see where the short time delay is set at to determine the number of cycles referecned above? For example if at 50kA the upstream breaker has its short time delay set at .5s then this 30 cycles delay is greater than the 3 cycle rating listed for 50kA. Do you then do the same comparison with 36kA and the upstream breaker to see if it complies?
I appreciate any guidance.
I'm trying to determine which of the two ratings to use for this ATS for the purposes of equipment evaluaiton. Do you have to look at the upstream breaker and see where the short time delay is set at to determine the number of cycles referecned above? For example if at 50kA the upstream breaker has its short time delay set at .5s then this 30 cycles delay is greater than the 3 cycle rating listed for 50kA. Do you then do the same comparison with 36kA and the upstream breaker to see if it complies?
I appreciate any guidance.