Laundry lighting on laundry circuit

Status
Not open for further replies.

deckscrew

Member
Can a laundry light and fan be put on the laundry circuit? I'm asking because the owner's would like to add more lighting and a fan to their laundry room. The washing machine, one receptacle and one light are currently on a dedicated 20 amp circuit.

Thanks
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
"No other outlets".

210.11(C)(2) Laundry Branch Circuits. In addition to the number
of branch circuits required by other parts of this section, at
least one additional 20-ampere branch circuit shall be pro-
vided to supply the laundry receptacle outlet(s) required by
210.52(F). This circuit shall have no other outlets.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
It means receptacle outlets in the laundry area into which the washer may or may not be plugged and which may have been considered by the code as suitable for an iron or other laundry accessories.
If that special circuit was not required by the code at the time the circuit was installed, the lighting outlet would be permitted and it would probably be OK to extend it to light and fan.
If it was never compliant, it might be necessary to pull a new circuit to pick up the existing light and the new lights and fan.

Tapatalk!
 

renosteinke

Senior Member
Location
NE Arkansas
Yes, just what is a "Laundry receptacle outlet?"

Since they say 'receptacle," I'd say that other types of outlets - like lighting outlets - are not allowed. An 'exception' would be a switch-controlled lighting receptacle outlet.

So, what's a 'laundry receptacle?' Please note that it does NOT say laundry 'area.' So, I'd say it's any receptacle positioned so that it can, in any way, be used for laundry-related activities. IMO, 'permitted' receptacles would be:
- Receptacles providing for ignition of the dryer;
- I'd stretch that to allow the receptacle serving the water heater igniter and vent fan, assuming the water heater is placed in the same area as the laundry;
-Receptacles providing power to the washer;
- "Convenience receptacles" placed in the laundry area;
-Receptacles providing power to irons, steam presses, and drying closets; and,
-Receptacles providing power to work counters in the area.

What receptacles would not be allowed to be on the laundry circuit? Well, I see these as being prohibited:
- Receptacle providing the furnace with power;
- Receptacles placed to meet 'convenience receptacle' requirements;
- Receptacles powering CATV and alarm systems;
- Any outdoor receptacles that you might be tempted to feed from a receptacle in the laundry area; and,
- Receptacles powering holiday lights, doorbell transformers, battery chargers, etc.

Please note I say "laundry area," and not "laundry room." This will require some discretion on the part of everyone. A full basement with a washer in one corner is not all "laundry room!" A closet with nothing in it but the machines, and no room for a counter or table, with the closet opening into a hallway might need only one receptacle to supply the washer. I do not see any requirement to try to guess where the 'iron' might be used elsewhere in the dwelling.

Let me use my own household remodel as an example:
Imagine a long, skinny room (7' x 14'). At one of the 'skinny' ends is the washer, dryer, and water heater. On the long walls, at the other extreme of the room, are doors providing passage from the house, through the room, and to the outside.
For the two long walls and the wall next to the laundry equipment, as I see it, every receptacle is allowed to be on the laundry circuit.
For the other short wall, we are required to place a receptacle from a 'convenience circuit.' IMO, since this area is open to the laundry room, it does not qualify as a hallway - yet, you're sure not going to place a table there! So, I see the code as prohibiting us from placing this receptacle on the laundry circuit.
 

n1ist

Senior Member
Location
Massachusetts
Occupation
Principal Electrical Engineer
In my kitchen, there's a 1.5 foot counter between the sink and the washing machine. I guess I need two receptacles there - one for the SABC, and one for the laundry area. Time to add the second one...
/mike
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
In my kitchen, there's a 1.5 foot counter between the sink and the washing machine. I guess I need two receptacles there - one for the SABC, and one for the laundry area. Time to add the second one...
/mike

Sorry, but since it is in the kitchen you are not allowed to have receptacles that are not on an SABC except for a few listed reasons, of which a laundry circuit is not one.
So as I see it the only recourse is to add an allowed third SABC which will also be the laundry circuit. It will have to meet the requirements for both circuit types. :)
But, on the bright side, it may qualify as the only receptacle circuit needed in that 1.5' wall space.

Tapatalk!
 

renosteinke

Senior Member
Location
NE Arkansas
I would differ ... the washer is in the laundry, and the stove is in the kitchen. There's no requirement that the two be in different rooms, or have a wall between them.

Unless ... the washer is one of those little things on wheels, which is temporarily hooked up to the kitchen sink faucet for use. Then, IMO, the washer is simply another appliance, and you don't have a laundry area at all. Now you get to invoke the "grandfather clause," in that a laundry circuit was not required before the 1996 code edition.

Two general observations:

A) Messes like this are why 'design' is outside the scope of the NEC- and the code panels need to back off!; and,

B) Architects seem to delight in "Clintonizing" codes, and making it real hard to apply general rules. What's a bedroom? A bathroom? A kitchen? Is the closet part of the bedroom, or the pantry part of the kitchen? And so on ...
 

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)
In my kitchen, there's a 1.5 foot counter between the sink and the washing machine. I guess I need two receptacles there - one for the SABC, and one for the laundry area. Time to add the second one...

Sorry, but since it is in the kitchen you are not allowed to have receptacles that are not on an SABC except for a few listed reasons, of which a laundry circuit is not one. ...

I would differ ... the washer is in the laundry, and the stove is in the kitchen. There's no requirement that the two be in different rooms, or have a wall between them. ...
Couldn't one draw a line on the ceiling and a cooresponding line on the floor and label the area "Laundry". Thereby defining which receptacles are "Laundry" and which are "SABC". (deleted comment about spontaneous ignition of the washer - I couldn't get the phrasing right)

... Two general observations:

A) Messes like this are why 'design' is outside the scope of the NEC- and the code panels need to back off!; and,
Yes - and other reasons as well

B) Architects seem to delight in cleverly defining (revised by ice) codes, and making it real hard to apply general rules. What's a bedroom? A bathroom? A kitchen? Is the closet part of the bedroom, or the pantry part of the kitchen? And so on ...
Depends on your definition of "is" ...

ice
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
I would differ ... the washer is in the laundry, and the stove is in the kitchen. There's no requirement that the two be in different rooms, or have a wall between them.
So, based on that simple analysis, if there is an 18" counter between the stove and the washer is it a kitchen counter or a laundry counter?
Does it require two receptacles because it is both?
Does it require one receptacle on each half?
Or does the owner get to identify the counter as one or the other based on their use of it?



Tapatalk!
 

n1ist

Senior Member
Location
Massachusetts
Occupation
Principal Electrical Engineer
I thought that would get some interesting discussion.

The washer is a regular one, not a portable. The more "proper" solution would be to put a duplex behind the washer (or dryer) and call that the laundry receptacle, and leave the counter one as a SABC and claim the it is part of the kitchen. In my case, the one GFCI is on a dedicated 20A circuit, so it can play either role. It likely is grandfathered, but I don't know when it was installed (the house is over 100 years old, but the GFCI certainly isn't). After all the mess I replaced when I bought the house, including flying splices insulated with duct tape, cut romex ends that were live, and the SEU that had lost all of the outer jacket, it's a minor issue.

/mike
 

kwired

Electron manager
Location
NE Nebraska
. Now you get to invoke the "grandfather clause," in that a laundry circuit was not required before the 1996 code edition.

Are you certain about that year? I started this trade using the 1987 code, and am pretty certain a laundry circuit was required then, there may have been some changes to what is permitted on that circuit but I remember needing to add 1500VA to load calculations for the laundry back in school, and that there had to be a 20 amp circuit for the laundry.
 