edlee
- Western Massachusetts
I did an emergency repair today , a hookup to a replacement compressor motor for a dry sprinkler system in a small mixed-use building. The old circuit was 15a 240v single-phase, 14-gauge copper, and the conduit run was about 25' long. The new motor draws nominally 7.35a @ 230v and the installation instructions called for minimum #6 copper conductors.
This seems offhand kind of crazy because I know it will operate on a much smaller wire. But the installers were concerned that if I used something smaller than #6 it might void the warranty. I talked to the local wiring inspector to see if there is something in the NEC referring specifically to sprinkler systems that I didn't know about and he didn't know of anything.
So we wired it in #6 thhn and put it on a 20a breaker.
Any thoughts about why they spec'd that?