mkgrady
 - Massachusetts
I need to run a three phase, 3 wire feeder to a rooftop chiller that requires 100 amps, 480 volts. The ceiling below the unit is very congested so I hope to run MC cable in lieu of conduit and wire. I will run to a JB below the roof and switch over to liquid tight from threre through the pitch pocket. Do they make 3-3 copper MC cable? Meaning 3 insulated and one ground wire. And would it be suitable for 100 amps? The terminals at each end are rated 75 degrees. I'd call my supplier and ask but they are closed this time of day.